SW+ Voltage Sag [RE-wrenches]
Matt Tritt
solarone at charter.net
Mon Aug 16 18:03:47 EDT 2004
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Get a Great Credit Card for You Today
You can find a credit card to fit your credit needs.
All types of credit cards -- 0% APRs, Rewards, & Bad Credit.
http://click.topica.com/caacvgubz8Qcsbz9JC9a/411Web
-------------------------------------------------------------------
Hi Ray,
I knew that it was theoretically OK to use 2/0 with 48 volt SW's but have
always been under the assumption that 4/0 was a requirement for the others.
This goes all the way back to SW's #0006 and 0007 that I put in back in the
stone age up to the last pre-Outback install. But then I re-read your
original message!
I guess I've been so out of touch with Brand X that I assumed you had
mis-typed the model #. If this inverter is indeed only rated at 2500 Watts
then 2/0 should be fine, but the only SW rated that low USED to be the 12
volt model.
My question SHOULD have been: Why aren't you using Outbacks? ;-)
Even a good running 4000 Watt SW will exhibit crappy performance when
starting a 1 kW submersible pump (if it starts at all). I think the problem
is that the inverter is just too small for the job, but it should run a
Staber just fine. Unless it won't. See the previous paragraph.
Matt T
----- Original Message -----
From: "Ray Walters" <ray at solarray.com>
To: <RE-wrenches at topica.com>
Sent: Monday, August 16, 2004 10:13 AM
Subject: Re: SW+ Voltage Sag [RE-wrenches]
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Amazing Diet Patch
The fastest - Easiest way to lose weight! Try it now FREE!
http://click.topica.com/caacvgtbz8QcsbadqCja/MyDietPatches
-------------------------------------------------------------------
Hi Matt;
The manual says 2/0 to 5 ft, 4/0 to 10 ft. I'm cheating by a foot or
two.
The 175 A at 24 VDC draw is 0.1 second peak from the circular saw; it is
not anything close to continuous run amps. Battery bank is 8 L-16s. DC
voltage at rest is 24.6v, surge drops the voltage to 23.2. Again, that is
a
0.1 sec minimum. I have always noticed batteries pull down like that for a
second on start up surges.
I'm going to change the cable to 4/0, but I don't think that is going to
fix it. I have a few of these SW + inverters installed with similar
complaints of lights flickering, etc when an inductive load comes on. They
all have 4/0 cable BTW.
Ray
> Hmmmmmm.
>
> You say that you're running a 2548 on 2/0 inverter cables. First-off,
my
>recollection about the SW 12 and 24 volt versions is that they actually
>require 4/0 cables to begin with becuase of the possibility of a 400 amp
>surge under certain startup conditions.
>
> It also sounds like the batteries are on the low side, which also
doesn't
>help much, but 175 amps draw? I hope this is on your Skillsaw and not the
>Staber. ;-)
>
> How long are your inverter leads and how big is the battery bank?
>
> What is the problem with the Washer?
>
> Matt T
> ----- Original Message -----
> From: "Ray Walters" <ray at solarray.com>
> To: <RE-wrenches at topica.com>
> Sent: Friday, August 13, 2004 10:46 AM
> Subject: SW+ Voltage Sag [RE-wrenches]
>
>
>
>
> Your free subscription is supported by today's sponsor:
> -------------------------------------------------------------------
> Need cash fast? Get a $500 CASH ADVANCE overnight! Let
> YourCashCentral get you the cash you need.
> http://click.topica.com/caacxycbz8QcsbadqCja/MyOnlinePayday
> -------------------------------------------------------------------
>
>
> >Dear esteemed colleagues;
>
> I am currently troubleshooting a Staber Washer control malfunction on
an
> Xantrex SW2524+ inverter. What I found curious is that the voltage
sags
> down to 88 VAC rms for about a tenth of a second during starting
surge. I
> am using a worm drive circular saw after to test. Measurements are at
the
> inverter AC terminals with a Fluke 89 set to normal MIN capture.(the
fast
> capture would get the bottom of the wave form itself) I also measured
the
> DC side and found the voltage to be 24.6 vdc at rest with the surge
>pulling
> it down to 22.9 vdc (again regular MIN capture on the Fluke). MIN
volts
>for
> 0.1 secs at the battery terminals was 23.2 vdc. The DC current surge
> measured at the shunt block with the Fluke was an amazing 175 amps for
0.1
> secs. AC current was harder to measure surge, but I saw a 27 amp peak
at
> the Inverter's onboard meter.
> My question is this: Is it normal to see a temporary voltage sag like
this
> when powering a heavy inductive load. I rechecked all my connections
AC
>and
> DC. I looked for volt drop at any tell tale points, etc. I am thinking
its
> an inductive issue with the DC cables, and so my next visit I wanted
to
> upsize the cables to 4/0 and twist the cables around each other.
>Everything
> else on the system seems to work great, other than occasionally a UPS
box
> for the computer beeps, again with a start surge from another
appliance.
> Your feedback, wisdom, comments, & of course criticisms are all
greatly
> appreciated.
>
>
> Ray Walters
> ray at solarray.com
> President, SolarRay, Inc.
> NABCEP Certified Solar PV Installer
> BS Mechanical Engineering, UT Austin 88
> Returned US Peace Corps Volunteer
>
> Your free subscription is supported by today's sponsor:
> -------------------------------------------------------------------
> Get a Great Credit Card for You Today
> You can find a credit card to fit your credit needs.
> All types of credit cards -- 0% APRs, Rewards, & Bad Credit.
> http://click.topica.com/caacvgubz8QcsbadqCjf/411Web
> -------------------------------------------------------------------
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
>http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>RE-GROW YOUR HAIR STARTING NOW.....Click here for more info!
>http://click.topica.com/caacxydbz8QcsbeuiVOf/Medical Hair Restoration
>-------------------------------------------------------------------
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
Ray Walters
ray at solarray.com
President, SolarRay, Inc.
NABCEP Certified Solar PV Installer
BS Mechanical Engineering, UT Austin 88
Returned US Peace Corps Volunteer
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Shop online for Discount Auto Parts: Mirrors Headlights Tail
Lights Bumpers Fenders Window Regulators Spoilers Altezza Lights
and a Full Line of Auto Body Parts. www.partstrain.com
http://click.topica.com/caacxygbz8QcsbadqCjf/Parts Train
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Save up to 67% on Omaha Steaks + Get 6 FREE Burgers and a
FREE Cutlery Set + Cutting Board!
http://click.topica.com/caacvgpbz8Qcsbz9JC9f/OmahaSteaks
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches