Ryan,

I think we need a clarification on the message from PV Powered. A single
circuit breaker cannot provide backfeed protection to two strings coming
into a PV array. The only reason you can put to strings on an SB2500U is
because it has been listed for NO backfeed. 15A of backfeed doesn't obsolve
you of overcurrent protection on the strings unless you only have one
string. Not many 2.8 kW systems only have one string.

Bill.


-----Original Message-----
From: Ryan Mayfield [mailto:ryan at energyoutfitters.com]
Sent: Monday, July 12, 2004 5:17 PM
To: RE-wrenches at topica.com
Subject: RE: PV Powered inverters-II [RE-wrenches]



Marco and Wrenches,

I apologize for not posting this earlier, PV Powered responded to the
question and I failed to post it for them. The following is their response
to the issue of back feeding and the over current protection for multiple
strings. Feel free to contact me directly with any questions.

Ryan Mayfield
Energy Outfitters

Our inverters do not back feed.  The inverter will only operate if a number
of safety conditions on the PV system and electrical grid are met, if not,
the inverter will never turn on.  Also, the inverters come with a DC circuit
breaker mounted inside them; thus, there is no need for external PV fusing.
The DC circuit breakers handle PV over current protection.

Best regards,
Brian Hoffman
PV Powered

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Amazing Diet Patch
The fastest - Easiest way to lose weight! Try it now FREE!
http://click.topica.com/caacoW6bz8Qcsbz9JC9f/MyDietPatches
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------







More information about the RE-Wrenches mailing list