Mo and William,
I would take anything that a Carlon representative said with a grain of
salt. They are in the business of saying that their product is as good or
better than EMT. Show me an unbiased engineering study done on the two and
we'll talk. Waterfront environments aside, most of California has extremely
low corrosion rates, and I would put my bets on EMT any day. Water tightness
is a hoax that I hope UL and others get away from. Water lives in outdoor
conduit systems regardless of their composition. That is why all conductors
must be wet rated.
I'll be seeing the San Diego inspectors at their annual meeting in a few
weeks, and I'll ask them about this issue. It doesn't make a lot of sense to
me. I believe that outdoor boxes and wiring systems need drains to allow
water to escape. Putting a better watertight fitting on a conduit is going
the wrong way in my book.
Bill.
-----Original Message-----
From: Mo Rousso [mailto:mrousso at heliopower.com]
Sent: Monday, March 15, 2004 3:31 PM
To: RE-wrenches at topica.com
Subject: Re: EMT - UL Heads Up [RE-wrenches]
>
> Following up on the PVC issue: I spoke to a representative from Carlon
> some time ago about UV resistance. Apparently it doesn't say that on the
> pipe for no reason. Any UV discoloration of PVC is only a few microns
> thick. It does not compromise the structural integrity of the product in
> any way. I'd actually like to have PVC on my roof for 20 years over EMT
> (especially in any marine proximity). Remember, beauty is only skin deep,
> but rust can go all the way through!
>
That's good to know about the PVC. And I agree with the rust issue. I
guess time will tell if PVC is a superior solution since we have put in
quite a number of these since the rule change.
--
Mo Rousso
President
HelioPower, Inc
760.451.9374
www.heliopower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list