Code issues (was adding MX-60's in PP) [RE-wrenches]
William Miller
wrmiller at slonet.org
Mon Mar 15 13:10:18 EST 2004
<x-flowed>
At 09:37 AM 3/15/2004, you wrote:
>Wrenches:
>
>When thinking about the "which side to connect to what" question you
>have to carefully consider the ampacity of the cables going to the
>battery AND the inverter. It is easy to end up with a Code violation if
>you do it the way Trace used to ? recommend. For those of you who
>remember the old APT power centers they had a 3 pole fused disconnect -
>1 or 2 poles for loads and a separate one for sources. This was the
>right way to do it but was not cost effective against the DC 250 due to
>the extra pole of OC protection. The basic problems are shown below:
>
>If you add load breakers by tapping in on the battery side, then you
>risk exceeding the ampacity of the battery cables. This is especially
>true with the combination of 4/0 and 250 Amp breakers which is already
>using the round up exception at 75C (breaker terminal temperature
>rating). Essentially, this means you can not add any additional load to
>the battery side. You should always connect additional load to the
>inverter side of the breaker. In this scenario the 250 Amp breaker is
>then acting as a main and doing it's job to protect the battery cable.
>With this method there is no impact on the inverter cable since it is
>already covered by the 250 Amp limit.
>
John:
Remember, if the MX60 is charging in tandem with the inverter, the
inverters constant-voltage charging circuitry should start tapering
immediately as it senses the increase in battery voltage caused by the
MX60. It seems highly unlikely that an inverter in charge mode, in tandem
with an MX60, could generate more current than the system, designed around
inverter DC loads, could safely handle.
I have always detested the mechanical ineptitude of connecting to the BACK
of the lugs on the DC breakers in the Xantrex disconnect. First of all,
the breaker hold downs are razor sharp and I have lacerated the heel of my
hand more than once. It is now SOP in our shop to file the bracket corners
on any new or existing installation. Secondly, the factory lead is too
small for any normal charge applications. Thirdly, how lame is it to have
to work behind the breaker???? A positive DC buss makes way more sense
here! (I shoehorn in a Square D LBA163104, if possible--tough if you have
a DCBB and a shunt.)
It seems to me like it is a no-brainer that one would connect charging
sources to the batteries with dedicated over-current protection. What if
one wanted to charge batteries from PV while the inverter breaker was
off? True also, the need to protect inverters, monitors, tracker controls,
DC loads, etc. from PV OC voltages. I can't see any argument to the
contrary that would overcome this logic.
William
PS: I did like the DC side of the APT units. The AC side made much less
sense.
William
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches