Jeff,
I'm not aware of an 1800 RPM 8.5 unit, unless it's really old. The 8.5 and
11 RMY units came out around 1999 with an air-cooled 3600 RPM 20- or 25-hp
OHV engine. They replaced the 6.5 RMY with its 1800 RPM flathead twin.
The 6.5 was a near-perfect match to back up a single SW inverter at full
capacity. They ran just about forever. The 8.5 is designed for
homeowner-grade backup power during occasional outages, and is sometimes
marketed with a G120-100 or -200 automatic transfer switch. It's not
well-adapted to backup charging, in that it just won't last under long hours
of run time under load. Our Kohler distributor has sent out cautions about
not using these units for prime power, as they are consumer-grade backup
units. We don't recommend them as backup for off-grid systems. Like Steve
Willey has said, the 10RY is Kohler's best unit for this application (at
~$7K).
Given all that, I think that the regulation electronics is the same between
the two units, so the problem you describe may be specific to that unit. We
had more than one unit arrive with a bad regulator. When running properly,
the 8.5s I have seen can run full current into one SW of any size, even
after our altitude derating of about 24% for 7,000'; this is more than the
6.5. Did a Kohler rep ever check out the unit?
Just my $.02.
Allan at Positive Energy
----- Original Message -----
From: "Jeff Yago" <jryago at wwjv.net>
> We recently replaced an 1800 RPM older model 8.5 with a newer version
> 3600 RPM unit. Client wanted to save money and the dealer was
> offering a really good deal as they were tired of driving 4 hours each
> way to service the older unit.
>
> Nothing else changed on this total off grid summer home in the woods.
> Same SW4024 inverter, same sixteen L-16 batteries, same Outback dual
> power point controllers, and same two separate solar arrays.
>
> BUT:
>
> As soon as the generator was replaced we starting having generator
> "error" lights on the inverter and the inverter would no longer
> complete a full equalize charge. We checked everything and lowered
> charging amps and generator capacity setpoints which helped some but
> did not completely resolve the problem.
>
> It is my belief that the low RPM Kohler had higher torque and spool up
> response than the 3600 RPM replacement, and regardless of nameplate
> rating, the newer unit was never able to meet the settings of the
> older model.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list