Inrush Current on 225 kW Inverter [RE-wrenches]
Bill Brooks
billb at endecon.com
Sat Feb 28 15:11:23 EST 2004
Joel,
I believe the package that Steven Engineering developed addresses this
issue.
Bill.
-----Original Message-----
From: Joel Davidson [mailto:joeldavidson at earthlink.net]
Sent: Saturday, February 28, 2004 9:09 AM
To: RE-wrenches at topica.com
Subject: Inrush Current on 225 kW Inverter [RE-wrenches]
We have PV system with a Xantrex 225 kW inverter and night-time switch. When
the system wakes up in the morning, the 340A, 480V load inrush current
causes the service panel circuit breaker to trip. The breaker is new and had
no previous problems. All connections are tight. Has anyone come up with a
capacitor or choke or other solution to "soft-start" high inrush current?
[Non-text portions of this message have been removed]
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://lists.topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list