SW firmware upgrade flourescent flicker [RE-wrenches]

Roy Butler, Four Winds RE roy at four-winds-energy.com
Tue Feb 24 00:49:41 EST 2004


<x-flowed>
I had the very same problem with one of my systems. Dual SW5548s, Onan 
20KW LP auto start genset, charging a Surrette 2700 AH/ 48 volt bank. 
The lights would flicker during the intial 15 minutes of each charge 
cycle. And then sometimes at several points during the charge cycle. 
Drove me and the owner kind of crazy.

What I found out was that by setting one SW max charge amps AC to 5 amps 
less than the other that we eliminated the problem. Of course now that 
we've replaced that system with a really sweet Outback system with 6-VFX 
3648 inverters with ALL the options, we no longer have that flicker!

My opinion is that it was definitely harmonics.

Roy Butler
Four Winds Renewable Energy, LLC
8902 Rt 46
Arkport, NY 14807
607-324-9747

Jeffery Wolfe, Global Resource Options wrote:

>Except that I have had the same pulsing light problem on a pre-GTI inverter
>for a couple of years. Only happens when the generator is running. We've
>replaced the genny, replaced the inverter (temporarily, with newer firmware)
>and given up. We believe it is caused by some weird load interaction between
>a load with harmonics (hard-wired smoke detectors required by code?) and the
>generator AVR (replaced that a couple of times). So at least in this case
>it's definitely not a GTI problem. I don't even really believe it's an
>inverter issue (Lights NEVER flicker with only inverter on.)
>
>Any other ideas?
>
>Jeff Wolfe 
>
>-----Original Message-----
>From: Christopher Freitas --- OutBack Power
>[mailto:cfreitas at outbackpower.com] 
>Sent: Monday, February 23, 2004 7:34 PM
>To: RE-wrenches at topica.com
>Subject: RE: SW firmware upgrade flourescent flicker [RE-wrenches]
>
>Thought I would share what little knowledge I have on the Xantrex GTI and
>this issue...  
>
>My undestanding is that this occurs when the GTI software is used without a
>GTI connected.  Internally the GTI includes a pass-thru relay which connects
>the AC loads directly to the grid when AC power is available.  If the GTI is
>not used or is connected incorrectly (or is not operating) than the loads
>are still being powered from the inverter which is pulsing its output as you
>describe as part of its islanding protection scheme.  
>
>So does the customer have a GTI box on the system?
>
>Christopher Freitas
>OutBack Power Systems, Inc.
>cfreitas @ outbackpower.com
>www.outbackpower.com
>Arlington WA USA
>Tel 360 435 6030  
>
>
>William Korthof wrote:
>  
>
>>I'm here but I haven't paid close attention to the software versions. 
>>The Brand X inverters definitely don't generate great interest, and I 
>>always kind of expect to oversights and "gee wiz" features. The 
>>inverters were originally put in around mid 2001 and just got the 
>>upgrades.
>>
>>/wk
>>
>>At 01:17 PM 2/20/04 -0800, Jerry Caldwell wrote:
>>    
>>
>>>Are any of the Xantrex guys still on list?  Do you guys have any 
>>>input regarding this issue?
>>>
>>>Jerry Caldwell
>>>Light Energy Systems
>>>510-205-2798
>>>
>>>--- William Korthof <wkorthof at earthlink.net> wrote:
>>>      
>>>
>>>>Yes, I've seen the same result. "upgrade" is definitely a 
>>>>misnomer.
>>>>
>>>>/wk
>>>>
>>>>At 05:45 PM 2/19/04 -0800, Jerry Caldwell wrote:
>>>>        
>>>>
>>>>>Wrenches,
>>>>>
>>>>>I have a customer who had his pre-GTI Trace SW inverters 
>>>>>retrofitted with the new anti-islanding software.  He claims that 
>>>>>ever since the upgrade
>>>>>          
>>>>>
>>>>his
>>>>        
>>>>
>>>>>flourescent lights powered by the backed up loads panel have a 
>>>>>flicker that pulses about once every second.  Sometimes the 
>>>>>flicker is worse than other times.
>>>>>
>>>>>Since the anti-islanding software is supposed to disconnect and 
>>>>>reconnect to the grid once per
>>>>>          
>>>>>
>>>>second,
>>>>        
>>>>
>>>>>I can't help but wonder if my customer isn't
>>>>>          
>>>>>
>>>>justified
>>>>        
>>>>
>>>>>by blaming the software upgrade.
>>>>>
>>>>>Has anyone had or heard of similar experiences?
>>>>>          
>>>>>
>>>>And
>>>>        
>>>>
>>>>>better yet, does anyone have ideas to solve this problem?  I want 
>>>>>to keep this customer relationship
>>>>>          
>>>>>
>>>>in
>>>>        
>>>>
>>>>>good standing.
>>>>>
>>>>>Jerry Caldwell
>>>>>Light Energy Systems
>>>>>510-205-2798
>>>>>          
>>>>>
>>>__________________________________
>>>Do you Yahoo!?
>>>Yahoo! Mail SpamGuard - Read only the mail you want.
>>>http://antispam.yahoo.com/tools
>>>
>>>- - - -
>>>To send a message: RE-wrenches at topica.com
>>>
>>>Archive of previous messages: 
>>>http://www.topica.com/lists/RE-wrenches/
>>>
>>>List rules & etiquette: 
>>>http://www.mrsharkey.com/wrenches/etiquete.htm
>>>
>>>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>>>
>>>Hosted by Home Power magazine
>>>
>>>Moderator: michael.welch at homepower.com
>>>      
>>>
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
>
>
>---
>[This E-mail scanned for viruses by Information Boulevard's Virus Scanning]
>
>
>
>  
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------



</x-flowed>


More information about the RE-Wrenches mailing list