hybrid grid tie [RE-wrenches]

Keith Cronin sales at islandenergy.net
Wed Feb 11 01:18:54 EST 2004


Bill
What is the real code issue? As long as it is labeled per NEC 690.54,56,
what other code items should I be addressing? As long as I have
documentation/plaques depicting the system and having the blessing of
the AHJ, where is listing dilemma? As long as I address 690.64 and
clearly layout where I am connecting to the supply side of the service
disco, there shouldn't be a problem.
If Chris and John or any of the manufacturers reps see potential
pitfalls with this technique before the debut of the Sunny Island, I
would like to hear their views.
Thanks Bill and all!

Keith Cronin
President
Island Energy Solutions Inc
318A Kuulei Rd
Kailua, HI 96734
808-262-3268 Tel
808-263-0338 Fax
www.islandenergy.net
 
 

-----Original Message-----
From: Bill Brooks [mailto:billb at endecon.com] 
Sent: Tuesday, February 10, 2004 1:16 PM
To: RE-wrenches at topica.com
Subject: RE: hybrid grid tie [RE-wrenches]

Keith,

Although these are very interesting technical discussions, I think you
are
faced with a very real code issue. Although the Outback unit may work
fine
in conjunction with an SMA inverter, I don't either are listed for that
type
of operation (Chris and John will be happy to correct me if I'm wrong).
When
the Sunny Island is available in the U.S., that situation will change,
but
until then, I think you are stuck. I think the best code-compliant way
out
of this mess is the previous suggestion of using the Outback MPPT charge
controller with a slightly higher voltage array (3, 24V modules in
series)
and some huge wire.

If the code is not an issue--go nuts--but remember this guy has a lot of
money to pay lawyers.

Bill.

-----Original Message-----
From: Marco [mailto:marco at pvthawaii.com]
Sent: Tuesday, February 10, 2004 11:00 AM
To: RE-wrenches at topica.com
Subject: RE: hybrid grid tie [RE-wrenches]


A number of years ago I purchased a device called a "Solar Maximizer"
from a
company in Australia, AES or AEI, I think.

****Buzz*** not listed--sorry--thanks for playing

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------







More information about the RE-Wrenches mailing list