Steve Willey, Backwoods Solar steve at backwoodssolar.com
Tue Jan 13 16:09:13 EST 2004


On the stacking question, where you have two 12 volt inverters and a 24 volt
bank, I would caution against a DC-DC converter.  While these allow taking
12 volts DC applications from a 24 volt bank, we find many converters fail
when the half-tap load is an inverter.  This is due to the ripple that is
imposed across the converter which it tries to follow and correct.  They run
really hot.

The other solution suggested, changing to different inverters to match the
battery voltage is one way, but a third way:  REARRANGE the battery bank to
a 12 volt bank, then use the Outback MX charge control to charge the 12 volt
bank from whatever 24 volt source you have.
Steve Willey,
Backwoods Solar Electric Systems
steve at backwoodssolar.com

Hi All,

Can I stack 2 Sw 2512's into a center taped 24v battery bank?

The reason as I'm sure you are going to ask is a friend with a really large
hydro, we are talking 200 amps at 12v from the hydro.  And he is trying to
improve that by going to 24v.

But he already has the SW's, hence the question.

Thanks,

jay

Peltz Power

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------






More information about the RE-Wrenches mailing list