transformer inrush [RE-wrenches]

Kirk Herander, VSE kirk at vtsolar.com
Mon Jan 5 12:26:18 EST 2004


Hello,

I have a SW4048 inverter used in a UPS mode to backup some household
critical loads - a septic and well pump and 2 fridges amongst others. The
system is always feeding the critical loads with grid ac through the
inverters transfer switch, supposedly rated at 60 amps. The surge potential
of the inverter is rated at 78 amps. The 120 vac output is fed into a
120/240 autotransformer, so 120/240 vac is supplied to the critical load
panel. My preference was to have only the 240 vac loads fed from the
transformer, but the electrician didn't set things up that way.

Twice in the last week the customer has called telling me that the inverter
has shut down due to an overcurrent error. It might be possible that
continuos plus/or surge currents from the critical loads could exceed 78
amps, but I'm wondering if the transformer could be adding to the problem.
If the primary of the transformer is constantly energized(core magnetized),
there should not be a high transformer-related inrush current, when a
motorized load turns on, adding to the surge requirement and creating the
overcurrent error, correct? Would it be helpful to just step up the voltage
for the sake of the 240 vac loads(water and septic pumps)?

Kirk

Vermont Solar Engineering
North American Board of Certified Energy Practitioners Certified Solar PV
InstallerT
Xantrex Certified Dealer Charter Member
Kirk Herander
PO Box 697
Burlington, VT. 05402
www.vermontsolar.com
www.backeastsolar.com
800.286.1252 - 802.863.1202
fax 802.863.7908

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------






More information about the RE-Wrenches mailing list