C35 Problem [RE-wrenches]
Mark Edmunds
mark.edmunds at xantrex.com
Wed Dec 3 17:17:47 EST 2003
Hi Louis,
It sounds like the micro in the C35 may be locking up, which can be caused
by the PV and battery lines being interchanged on the unit, though this will
normally be immediate, not 2-10 minutes. Worth checking anyway. While you
are checking, make sure the jumpers are installed in the correct locations
for your battery voltage. Also any chance the unit is hitting an over
temperature limit? If this was the case you would see the orange overtemp
LED indication, it doesn't sound like you are.
Regarding the question on the voltages on the input and output: The
controller works like a series switch but uses FETs to do the actual
switching. So the voltage across the unit from the PV to Battery terminal
while bulk charging should be near zero, as you saw.
I will get an Engineer to contact you off line to give you a hand.
Regards,
Mark Edmunds
Xantrex Technology Inc.
-----Original Message-----
From: Louis Woofenden [mailto:louiswoof at hotmail.com]
Sent: Tuesday, December 02, 2003 6:28 PM
To: RE-wrenches at topica.com
Subject: C35 Problem [RE-wrenches]
Hi,
I've just run into a problem with a Xantrex C35 charge controller, and I'd
like to know if anyone has experienced a similar problem. This problem
occurred with three different units, which would seem to point to the
installation, or something in the surrounding system, but I cannot find
anything. A call to Xantrex tech support yielded no useful information.
Anyhow, here's the problem:
When I apply power from the battery to the controller it turns on normally,
and starts to regularly blink a single blink. When I turn on the array
charging current (about 13 amps @ 12 volts), the controller will charge for
2-10 minutes, and then will simply quit. No lights, no charge current, etc.
If I disconnect the controller for a few minutes, I can repeat this cycle
when I reconnect.
The controller is installed in a system running fans for a remote restroom.
Other loads on the system include a 120v sump pump running off a 2.5 KW
mod-sine inverter (controlled by a solenoid), and a few lights on a timer.
The only other piece of equipment in the system is an old meter, which is
measuring the voltage, array current, etc.
Oh, one more thing. Can anyone tell me what the difference is input vs.
output voltage should be on a C-series controller? I'm seeing a difference
of about .05 volts between the input from the PV, and the output to the
battery. Is that about right?
Any ideas would be much appreciated.
Best,
Louis Woofenden
The Solar Store
Tucson, AZ
_________________________________________________________________
Get holiday tips for festive fun.
http://special.msn.com/network/happyholidays.armx
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list