Inverter charges do have substantial AC ripple current components on their
dc input, and I agree with John B., the 28A is probably an estimate of what
the impact on total rms current will be. I look forward to seeing what John
Wiles can say regarding this. In the past the assumption has been that the
NEC 1.25 factor will cover for this extra heating effect.
Either way the efficiency number to use for the SW when doing cable and fuse
size calculations is 85%, which represents worst case operation with a
combination of low battery voltage (at the low input protection level) full
power output, and maximum ambient temperature. There is slight variation
from unit to unit, but this is close. Page 131 of the SW manual has this
already worked out, as a helpful guide - you can find the manual at:
http://www.xantrex.com/support/docserve.asp?id=602
<http://www.xantrex.com/support/docserve.asp?id=602>
Regards,
Mark Edmunds
Xantrex Technology Inc.
-----Original Message-----
From: John Berdner [ mailto:jberdner at sma-america.com
<mailto:jberdner at sma-america.com> ]
Sent: Friday, November 28, 2003 12:02 PM
To: RE-wrenches at topica.com
Subject: Re: SW inverter to battery cable calculation [RE-wrenches]
Wrenches:
I "think" I know the answer Joel's question about where the extra 28
Amps comes from.
I would guess it comes from experimental data.
I will ask J. Wiles and forward his reply.
In the interim I will try to shed some light.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list