Hi JeffO'
We have got the local inspectors to agree that these are not back feed
breakers, they are "intertie breakers".
Backfeed breakers can have current on both sides when disconnected. When
you turn off a backfeed breaker the feed side remains energized.
Intertie breakers cannot have current on both sided when disconnected.
When you turn off an intertie breaker the inverter side denergizes. The
breaker operates as intended with intertie equipment, the wire is
protected and
No hold down required on an "intertie breaker"
Jeff Oldham wrote:
>What kind of clever methods have you all found for backfeed breaker hold-downs on residential panels to meet code and aware inspectors? Many manufacturers don't offer anything. Some inspectors are not buying the dead front cover.
>
>Thanks,
>-jeff o
>
>
>>From the Solar, Wind and Hydro powered office of Jeff Oldham
>
>________________________________________________________________
>The best thing to hit the internet in years - Juno SpeedBand!
>Surf the web up to FIVE TIMES FASTER!
>Only $14.95/ month - visit www.juno.com to sign up today!
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list