Robust battery [RE-wrenches]
Brad Bassett
bsbassett at earthlink.net
Sat Nov 8 19:24:46 EST 2003
Back at a previous place I worked, we installed a good number of
Absolyte battery banks. A few more observations:
They lasted about 7-8 years in solar applications, with some hybrid
input.
Although their literature says they are freeze tolerant, don't believe
it. Even following their instructions I've never seen one recover from
being frozen. Also it can be dangerous to charge a frozen battery.
Although their literature says they are tolerant of extended periods
with a partial state of charge, don't believe it. If they are not fully
recharged just like other lead acid batteries they will lose capacity
and their positive plates grow at a prodigious rate. I've seen broken
cell casings from plate growth. I tried to get my bank to last through a
northwest winter without generator backup, and the battery had less than
25% capacity the next spring. I was not able to recover any more. I then
got into a cycle where trying to equalize the battery to recover
capacity just made the plate growth worse.
Voltage set point is very specific in relation to daily depth of
discharge to maintain the warranty, but at least they recognize that a
higher voltage is desireable when cycling is deeper. Still, in the
telecom systems we'd set the regulation point at 2.46v /cell for on/off
controllers (14.8 for 12 nom). I think they like the higher voltage to
fully recharge, but it may void the warranty to charge at higher
voltages than the recommendation. We never had a problem with electrlyte
dryout that they are noted for, but I think that happens when they are
in float service.
Sometimes you can remove the cells from their steel case to transport
the battery into spots where vehicles can't get in, sometimes, depending
on a number of factors like altitude, temperature, how rough you want to
get, etc. The factory doesn't recommend it but are aware that it
happens.
Absolytes are indeed good batteries for the reasons pointed out by Dan.
I just thought I'd clarify a few points in case someone thought they
were miracle batteries. Guess I'll go out and water my L-16's now.
Brad Bassett
Alternative Energy Eng.
Olympia, WA
brad at alt-energy.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list