c-40 battery charging [RE-wrenches]
Bruce Geddes
b.geddes at clear.net.nz
Fri Oct 10 17:30:22 EDT 2003
Perhaps there is some reason that I am unaware of but the simple act of
connecting strings to a buss bar electrically will not produce any better
current sharing than paralleling strings in the bank. The only reason I can
see for a current imbalance in a bank is if the interconnects are too small
so cable resistance means the first string takes more juice. Also dirty
posts creating high resistance joints will have a part to play.
So assuming good cable sizes and clean joints, I see no electrical gain by
using a buss.
In a Telco installation the buss will allow one string to be taken out of
service without disrupting the rest and this is perhaps a valid reason to
connect this way.
If connecting with multiple strings I would certainly suggest using a fuse
or breaker on each string with AGM/gel cells as the previous mails on
thermal runaway have shown the downfalls. Connecting via a bus will not
overcome this problem.
Cheers,
Bruce Geddes
PowerOn
> I think that with multiple strings the buss bar plan is the way to go to
> avoid having to fuse each string. If there is no reason for any one
> string to take too much current the need for an individual string to
> have a fuse is negated. This is so weird. I used to connect all my
> parallel strings to a common buss until just a few years ago. A big
> battery guru told me it wasn't necessary.
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list