>Thanks for the explanation of how an online UPS can also be a non phantom
>load. Sounds like some energy efficient design went into these boxes.

Strange.  I came to the exact opposite conclusion.  If the 
ferro-resonant transformer is energised all the time then that will 
be a big phantom load.  They are nice things to work with because 
they are so robust but hopeless for 24 hour power supplies with 
variable power loading.

At 4:58 AM +0000 7/9/03, Robert Warren wrote:
>for a PV-UPS, you have about a 10 to 12% loss due to heat and magnetic
>saturation of the ferro transformer. If you can live with that, it is
>worth looking into. However, this efficiency is if you are at 70 to 90%
>of capacity with your load. If you have a load rated at a lot less than
>this, the efficiency goes to hell, as you are on the low end of the
>output efficiency curve.


-- 
Hugh

http://www.scoraigwind.co.uk/

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------

</x-flowed>


More information about the RE-Wrenches mailing list