The higher your battery voltage is going into a modified sine wave
inverter, the higher the peak voltage is on the output. To compensate
for this (regulate 120v rms) we narrow the width of the pulse. Some
loads may not like either the high peak voltage or the narrow pulse
width or both. When it comes to mod sine compatability, there are three
kinds of loads, 1. Ones that work 2. Ones that don't work and 3. Ones
that work dependant upon battery voltage. It sounds like your sensitive
loads fall under #3.
Roy Dyngen
Christopher Freitas - OutBack Power wrote:
>
> You should check the RMS voltage and peak AC voltage when the inverter
> is running with a light and heavy load. The RMS voltage should be
> 120VAC +/- 10V under all conditions but the peak voltage should be
> between 180V and 140V. There are a couple of failure modes that can
> result in the behavior you are seeing.
>
> Most likely it needs a new FET board. Getting someone with a O-scope to
> check it is probably the best way to check it.
>
> Christopher Freitas
> OutBack Power Systems, Inc.
> cfreitas at outbackpower.com www.outbackpower.com
> Tel 360 435 6030 Arlington WA USA
>
> jay peltz wrote:
> >
> > Hi All,
> >
> > I've got a DR inverter that is doing the following.
> >
> > When voltage above around 13.8v ( 12v system) the inverter will not run
> > electronic items, it'll do lights and toaster etc, but not the TV, radio
> > etc.
> >
> > Any ideas? or is this back to the factory?
> >
> > thanks,
> >
> > jay
> >
> > Peltz Power
> >
> >
> >
Roy Dyngen
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list