HU361 as Combiner/Disconnect [RE-wrenches]

John Berdner jberdner at sma-america.com
Tue Jun 3 17:03:51 EDT 2003


Wrenches:

Square D told me that the lugs ARE approved for 2 wires per lug but in
some weird combinations.
1 AWG #10 solid and 1 AWG #12 stranded, etc.
I explained the intended use and suggested they change it to all
combinations of 1 each AWG #10 to AWG #14 stranded or solid. 
They said they would do this (it is a simple mechanical pull test) but
I have not seen anything further on it.
I'll follow up withthem and see whas up.

Regards,

JSB 

>>> clrwater at earthlink.net 6/3/2003 11:45:10 AM >>>
Hi Matt,


Yes I see your points.  I was trying to get away with only one line 
to the SB by combining a the HU361  but if each lug is rated for only 
one cu landing that won't work and it defeats what I was after.

But it strikes me as very odd that a PSSB breaker can be rated to two 
conductors/lug but not the nice big lugs on a HU361.  Any chance of 
that rating changing?  John B?

Thanks,

Jeff C.


>
>1.  The Line (Array) is required to be landed on the top lugs of the
>Disco. (Behind the arc-shield)

My drawing was electrical not orientation - but yes thanks for the 
reminder of using the shieded side correctly.

>
>2.  The lugs are rated for single-conductor landing only.
>
>My recommendation, at least relating to the Disco at the Inverter, is
to
>run the two "switched hots" (from the bottom lugs) to the SB.  The SB
>has 3 DC Input terminals for a reason.  This is it.
>
>Regarding the use of an HU361 at dual locations, I think you will
find
>you can easily run the extra pair between disconnects in the same
>conduit you are already installing.
>
>Try it this way:
>
>ARRAY
>
>+ from String 1
>            + from String 2
>l         l
>0   0   0
>
>      ROOF Disco
>
>0  0  0
>l       l
>l       l
>l       l
>+      + to 2nd Disco; Line 3
>to 2nd Disco; Line 1
>l       l
>l       l ________ IN CONDUIT
>l       l
>
>
>+ from Roof Disco; Load 1
>            + from Roof Disco; Load 3
>l         l
>0   0   0
>
>      INVERTER DISCO
>
>0  0  0
>l       l
>l       l
>l       l
>+      + to SB DC Input
>to SB DC Input
>
>
>Hope this helps...
>
>Pray for Sun and No Tanlines!
>
>Matt Lafferty
>Universal Energies Institute
>mlafferty at universalenergies.com 
>(916) 422-9772
>(916) 628-7694 Cell
>(916) 914-2247 Fax
>www.universalenergies.com 

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================





More information about the RE-Wrenches mailing list