William,

I believe that the C-40 isn't actually protected by the 250 amp inverter
breaker, it's only used as a disconnect from the batteries. The fact that
there is a 30 amp input breaker has to do with the original array size at
time of order, not what the controller is capable of. One interesting result
of this wiring scheme is that, if you think you have cut power to the
inverter by turning off the main breaker, but have not shut off the
controller input, the inverter still has DC power in!

I usually run the controller output (never a C-40 these days) through
another breaker of equal value to the input side before connecting to the
battery.

Matt T----- Original Message ----- 
From: "William Miller" <wrmiller at slonet.org>
To: <RE-wrenches at topica.com>
Sent: Friday, May 09, 2003 2:19 PM
Subject: Over current protection for charge controllers [RE-wrenches]


> Friends:
>
> I know this has been covered before, but in a different context.  I am
> installing a Xantrex Integrated Power Panel.  It has one C-40 charge
> controller. The battery positive lead connects to the bottom of the GJ250
> circuit breaker.  The top of the breaker connects to the inverter AND to
> the C-40.  Shouldn't the C-40 have over current protection of a lower
> value?  It is protected now at 250 amps.  I figure it needs to be about 60
> amps (40*1.56=62.4).
>
> Also, Xantrex prewires the C-40 input through a 30 amp DC breaker.  This
is
> not right either, to my knowledge.  That breaker should also be 60 amps.
>
> I don't know if we have a Xantrex rep. on the list anymore.  I hear Pagan
> is gone, and, as I recall, Ezra also.  It would be nice if Xantrex
> responded, but I of course value input from the rest of you
> installer/engneers.
>
> Thanks,
>
> William Miller
>
>
> __________________________________________________________________
> William Miller
> Miller Power and Communications
> PO Box 50, Santa Margarita, CA 93453
> Voice :805-438-5600     Fax: 805-438-4607
> email: wrmiller at slonet.org
> http://millerpowerandcomm.com
> License No. C-10-773985
> _____________________________________________________________
> Compatibility:
> Word processor: WP10
> Spreadsheet: Quatro Pro 10
> CAD: Microstation 95, DXF, Visio 4.1T
> _____________________________________________________________
> "Every decent man is ashamed of the government he lives under."
>                                     H. L. Mencken
> __________________________________________________________________
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================





More information about the RE-Wrenches mailing list