If the readings are about equal during static condition (no charging,
no load current either), but the differences increase with the
current, then it's because of resistance between the different
measuring points, which causes voltage drop in proportion to the
current.
You can take a multimeter and read V between the + connection point
of one metering device and + point of another device, and it should
show the difference, which should increase in proportion to the
current between those points. You can do the same between the
negative points.
If there is a corroded connection, measure from one lug of the
connection to another lug (for example) while current is flowing, and
if there is excessive resistance, you will read the voltage drop on
your meter.
All this might lead you to discovering where the unwanted resistance
occurs, without unnecessary wrenching.
Windy
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
</x-flowed>
More information about the RE-Wrenches
mailing list