Keith,

Careful with the definition of "source". The code thinks a source is
something that has no controls like a generator or utility power being fed
from another panel. Inspectors get confused all the time.

Our PV inverter is essentially a negative load. Which way does the current
flow? Trick question--it's AC. All this stuff about backfed breakers and
direction of current flow is somewhat irrelevant. The utility is a VERY BIG
voltage source--put it on the line side so the load side is dead when the
switch is open. As you point out, the meter has to read power flow in the
proper direction so we connect the line side of the meter toward the
inverter.

Hope to see you soon in Kona. Catch a wave for me.

Bill.


-----Original Message-----
From: keith [mailto:kcronin at lava.net]
Sent: Thursday, March 06, 2003 12:22 PM
To: RE-wrenches at topica.com
Subject: RE: AC disco Wiring? [RE-wrenches]


Graham

I believe the wiring should be on top.  We always use the top for LINE
installations on disconnects.  Since the PV/inverter is technically the
source, and the utility is the "load", that's were I have been
accustomed to landing the wires.
NEC: 380-6C

Check the exception...!!

The electric meter should definitely be in the line/top position for the
main service.  I was spanked at the age of 20 from an electrical
inspector from that and will never forget it!

My 2 coconuts!

Keith Cronin
Island Energy Solutions
318 A Kuulei Road
Kailua, Hawaii 96734
808-262-3268 Tel
808-263-0338 Fax
www.islandenergy.net



-----Original Message-----
From: Graham Owen [mailto:graham at solarexpert.com]
Sent: Thursday, March 06, 2003 9:33 AM
To: RE-wrenches at topica.com
Subject: AC disco Wiring? [RE-wrenches]

>From looking at numerous PV installations I have noticed that the
wiring
of AC disconnects can be done in two different fashions.  Is it best to
land the wires from the inverter or the wires from the service panel on
the top of the switch?  I had been landing my wiring from the inverter
on top, but I think this may be incorrect, even though all systems have
passed inspection.  It now seems to me that the wires from the main
panel are always hot and should land on top?

Graham Owen
GO Solar Company

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================






More information about the RE-Wrenches mailing list