600 VDC switches [RE-wrenches]
Tom Lane, Energy Conservation Services
tom at ecs-solar.com
Mon Feb 10 21:46:17 EST 2003
thank you gator tom
----- Original Message -----
From: <jberdner at sma-america.com>
To: <RE-wrenches at topica.com>
Sent: Monday, February 10, 2003 9:36 PM
Subject: RE: 600 VDC switches [RE-wrenches]
> Guys:
>
> Yes, this is good news from Square D.
> We have been working on this one for over a year.
> Now that it has come to pass I want to jump in and take some credit.
> I know it is shameless, but I can't resist - sorry ;-)
>
> Many people were involved but Tom Keene at Square D deserves most of the
> real credit. He was a great champion for our industry inside Square D
> and I do not think we could have done it without his support.
>
> First we had John Wiles and SWTDI run some tests for us and, based on
> John's data, it looked like the 361 could do 13 Amps.
> Then Marv used the results to develop and get UL approval on a whole new
> test procedure specifically for PV system dc disconnects. This was
> bucking tradition and was a lot harder than it sounds. Thanks to Tim Z.
> at UL for the support on this one.
>
> Then we had to get Square D to run the procedure that UL approved.
> Then we had to get Square D to run it again since they ran the old
> switch procedure by mistake and the switch did not pass the test that we
> already knew it would not pass (90 Amps at 600 Vdc for 50 cycles then
> 2000 cycles at 30 amps and 600 Vdc).
> In the middle of all this Square D legal got involved and side tracked
> the whole thing for about 3 months. This snafu was why we stopped
> recommending the HU361 for a couple of months.
>
> Bottom Line - 1 switch can be the disconnect for up to 3 inverters. One
> more point - The lugs are UL approved for 2 wires in each lug!
> The two positive strings can be combined in the switch with a single
> positive going out of the switch to the inverter. The two negatives
> just pass through the switch uninpterrupted and land on 2 of 3 negative
> terminals in the inverter.
>
> Now I am trying to get some UL documentation on the new ratings for the
> switch from Square D. Once we get it we will post it on our website or
> tell you how to find it on Square D's. The UL file reference in E.H.'s
> post does not show the new ratings yet.
>
> The next step is to get UL approval for a combination DC and AC
> disconnect in the same switch.
> 1 pole for PV positve / polymeric divider for seperation of circuits / 2
> poles for the 2 ac hots. If we can get that, we have 1 disconnect that
> is both the ac and dc disconnect and meets the utility requirements.
> Keep your fingers crossed.
>
> If you have any questions, or if I can be of any further assistance,
> please do not hesitate to contact me.
>
> Best Regards,
>
> John Berdner
>
> SMA America, Inc.
> 12438 Loma Rica Drive, Unit C
> Grass Valley, CA 95945
> 530.273.4595 (voice)
> 530.274.7271 (fax)
>
>
> -----Original Message-----
> From: Mangelsdorf, Marco [mailto:mmangelsdorf at hei.com]
> Sent: Monday, February 10, 2003 4:10 PM
> To: RE-wrenches at topica.com
> Subject: RE: 600 VDC switches [RE-wrenches]
>
> Good news, indeed. From what source can we get this bugger? Will it be
> immediately available?
>
> marco
> ProVision Technologies
> Hilo
>
> Wrenches,
>
> Good news from Square D on this thread. I found out today that Square D
> has
> received UL approval for use of the HU361 in PV systems up to 600VDC and
> not
> more than 13A per pole (no series switching or negative switching is
> required - 3 poles, 3 positives). See letter from Square D below.
>
> E. H. Roy
> Solar Works, Inc.
> 64 Main Street
> Montpelier, VT 05602
> 1-800-339-7804 ext. 306
> ehroy at solar-works.com
>
>
> DATE: 2/10/03
> TO: E. H. Roy - Solar-works, Inc
> FROM: Bob Miller - Square D Company
> SUBJECT: Photovoltaic application of Safety Switches
>
> E.H.,
>
> Square D Company has obtained UL listing (File E2875, Vol. 1) for 30 amp
> non-fused heavy duty switches, HU361, HU361RB, HU361AWK and HU361DS,
> for
> use on photovoltaic systems. The 2002 National Electrical Code does not
> allow the negative conductor to be broken when operating switches on
> photovoltaic systems. The above mentioned switches may be used on
> photovoltaic systems as shown below as long as the line voltage per pole
> does not exceed 600 Volts DC and the normal rated current per pole does
> not
> exceed 13 Amps DC.
>
> Bob Miller
> Application Engineer
> Square D Company
> 859-243-8069
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-Wrenches
mailing list