Hi Clive,
                I agree with your comments.  Do you have any idea about this
belief that the first cell on the +ve end of the battery (or in some cases
the -ve end) is the first to fail?  I have seen this idea promoted
frequently but have never found a good explaination for it and it does not
seem to stack up electrically.  I have seen cells fail randomly through
batteries so think it an urban myth.

Cheers,
Bruce

> Hi Bruce,
> Three things  that cause the pos. plate to bulge: overcharging, too long
on
> float duty ( batteries on float duty should have a periodic discharge test
> to check that they do in fact have the capacity to do the job they are
there
> for ) Equilise charge too often..
> The pos. plate always corrodes first. To counteract this inhibitors are
> included  in the mix. and   pos. plates is cast under high pressure to
make
> it more dense than the neg.
> The Plante type cells had  pure lead plates with no inhibitors, but they
> were design for float duty.
>  Cheers Clive
>
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------





More information about the RE-Wrenches mailing list