SMA- SB voltage window [RE-wrenches]
John Berdner
jberdner at sma-america.com
Mon Oct 27 12:56:14 EST 2003
Keith:
The Sunny Boys can be adjusted but we require a letter from the utility
that authorizes the changes for that specific installation (serial
number(s) and location). We have done this for a few customers with
very specific issues and only with the knowledge and buy-in of the
utility.
I must point out however that voltage limits were developed for a
reason.
If you crank the voltage up you will reduce the life of other loads at
the site, e.g. light bulbs, motors, etc.
If you change voltages without the utility permission and they find out
about it they can lock you off their system.
Contact me off line if you have additional questions.
Best Regards,
John Berdner
>>> kcronin at lava.net 10/26/2003 01:09:10 PM >>>
Hello
Does anyone know if the Sunnyboy 2500 is field adjustable for the
voltage window to be expanded like the Xantrex large units are?
Thanks
Keith Cronin
President
Island Energy Solutions
318A Kuulei Rd
Kailua, HI 96734
808-262-3268 Tel
808-263-0338 Fax
www.islandenergy.net
--
[Non-text portions of this message have been removed]
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list