A mystery to me..... [RE-wrenches]

Jay Peltz, Peltz Power jay at asis.com
Mon Oct 20 21:50:45 EDT 2003


HI all,


I think that its time to get the clamp on amp meter here.  You should be
able to pinpoint the  bad connection via that.  I do agree that the problem
is a bad connection ( battery cable) or a bad cell..  Also you should be
able to increase the load and measure the voltage drop and find the problem.

Please keep us informed as to what it turns out to be!!


jay

Peltz Power


----- Original Message ----- 
From: "Roy Dyngen" <roy.dyngen at xantrex.com>
To: <RE-wrenches at topica.com>
Sent: Monday, October 20, 2003 10:48 AM
Subject: RE: A mystery to me..... [RE-wrenches]


> Hello Daryl,
>
> I would agree with those that are pointing to the batteries/cables as the
> source of your problem.  If it were not a battery/cable issue, with a
> voltage drop as large as you are experiencing, it would mean an awful lot
of
> power being dissipated somewhere.  If this was not in loads and internal
to
> the inverter, I believe the smoke would have been let out of the inverter.
>
> Roy Dyngen
> Xantrex Technology Inc.
>
> -----Original Message-----
> From: penobscotsolar at midmaine.com [mailto:penobscotsolar at midmaine.com]
> Sent: Saturday, October 18, 2003 2:19 PM
> To: RE-wrenches at topica.com
> Subject: A mystery to me..... [RE-wrenches]
>
> Hello all,
>    I'm having no success in troubleshooting a system we installed almost
two
>
> years ago that is three hours travel time each way. It has operated
> flawlessly since installation. We have had no lightning in the area for
> months.
>    The system is an SW4048-PP with 24 Surrette KS-25 batteries. It was
> originally set up for generator only use (against my recommendations) but
> they quickly added a 1.2 KW array within the year. We aded an Outback
MX-60
> to the system this last July.
>    I arrived at the site with replacement inverter in hand. We started up
> the original inverter with manual bypass breakers both off. It ran fine,
> starting up and going into search after 20 seconds or so. Setting it to
ON,
> again, it ran fine. We turned off the main in the house and threw the
> inverter breaker in the bypass and it continued to run fine. We turned off
> all the breakers in the main panel and turned the main on and it ran fine.
> We threw the first breaker and it continued to run fine. We turned off the
> first breaker and continued in this manner until we threw a breaker (
> labeled track lighting) and I saw the battery voltage suddenly drop from
> 54.4 volts to 27.2. The inverter shut down with no error reading and
without
>
> any breaker tripping anywhere. We shut off this breaker and turned the
> inverter back on. It ran fine.
>     We continued on and found 2 breakers which powered sub-panels both had
> the same effect. One sub powered a Grundfos 1/3 hp SQ-O series 110 VAC
> submersible, among other things (mostly lights in the room where the sub
> panel is). It seemed as though certain loads were dragging the inverter
> down.
>     To shorten this story, we replaced the inverter and voila! the same
> problem!!!!!
>     When they power the house with the generator through the manual bypass
> switch everything runs fine. The system has separate structure ground (for
> the array) and system ground (the electrical systems ground)
>      WHAT AM I MISSING???
> Daryl
> Penobscot Solar Design
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------





More information about the RE-Wrenches mailing list