Assuming you are using a single SW5548 - it is very marginaly.
The "locked rotor amps" off the Franklin Electric chart says 34.2 amps @
240 vac - so it would be 68 amps+ on the 120 VAC side. This puts it
very close to the 78 amp RMS output limit on the SW series. Might work
- but what about when the wash machine or microwave is running?
Here is a good site to reference for pump motor specs:
http://www.h2oguy.com/pumpsys/feelecspec1ph.html
Running a step-up T-240 transformer for the other well pump is not out
of the question - but a second inverter would be another option. I am
sure you could put in another switch (float or pressure) that would then
power up the transformer and pump with 240 VAC and then its control
would engage.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com www.outbackpower.com
Tel 360 435 6030 Arlington WA USA
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list