12 VOLT controller [RE-wrenches]

Pat Redgate solarpro at aol.com
Mon Oct 13 23:59:20 EDT 2003


In a message dated 10/13/2003 7:17:47 PM Pacific Standard Time, 
allan at positiveenergysolar.com writes:

  "The problem I see with the approach you have described is that it allows 
the> PV pump to        shut off at high storage tank temperature"

        Preventing overheat problems is, has and ever shall be a problem.  It 
is best solved by proper sizing, orientation and tilt.  This is the best 
reason for elevating panels to a higher angle (to stop overheating, rather than to 
be enhancing performance).   Also, black chrome kills.
 
        "I would rather see no high-limit shutoff, and rather a thermostatic 
mixing valve to prevent overheating. How do you handle this?"
        
       
       To set an upper limit or not to set an upper limit; that is the 
question...   What fails on a solar water heater first?  It seems, much to my 
surprise, to be the tank.  The panels can take the heat, so can the copper tubing 
and pump; but the tank goes into hyper-oxidation above 165F.  Maybe your fluid 
needs replacing more often, but it sure beats rolling out a new tank every five 
to ten years.  BTW, how does a thermostatic mixing valve prevent overheating 
IN the tank?  Tempering valves are required in our part of the world - they 
prevent scalding water from entering the household.  The guts of the valve need 
periodic maintenance and most fail by mixing in too much cold water, thus 
diminishing the solar contribution.  But they do work well as hot water extenders 
when they are new.  

As far as the PRV is concerned...  You do not need one (I know, code) if the 
system is sized correctly.  If you do use one, DO NOT install it anywhere near 
the solar collector.  If you must, put it in the loop downstream and vent it 
to grade.

But, every SHW solution is site specific.  I am lucky, with 95% of our 
systems located within 75 miles of the coast and the BEST weather in the world, I 
have very little to worry about.

Surfs up.

Patrick A. Redgate
AMECO
Long Beach, CA
(562) 595-9570
www.amecosolar.com

--
[Non-text portions of this message have been removed]

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------





More information about the RE-Wrenches mailing list