Mo,

I think Matt did the best job yet of laying out the fundamentals. He's got
the doughnut to inspector ratio dead-on.

I'm sure you all see more fast-bucks in CA then we do over on this coast but
I've sure seen a few examples of less than minimum installations. Here's my
top ten besides the typical electrical hack issues:

1) Auxiliary ground rods not bonded to building's grounding electrodes.
2) Modules and racks not grounded (which renders the GFI protection
ineffective)
3) Romex used to connect modules (true story!) or other improper conductors.
4) Conductors and conduits not strapped on roof (out here this really
becomes an issue with snow and ice)
5) Improperly rated equipment and/or connectors, particularly for higher
voltage DC
6) Lack of adequate labeling on boxes, disconnects, etc.
7) Lacking or improper fusing of parallel module strings (tough one to
address in a quick session)

I couldn't reference the code on these but I think they illustrate
unjustified safety and reliability issues in PV installations. I expect
there will be some disagreement here:
8) Wood used as racking materials in roof-mounted arrays
9) Single conductor cables with plug connectors used on high-voltage
ground-mounted arrays accessible to general public.

And my personal favorite:
10) Using the homeowner's ladders when installing systems.


Keep up the good work!

Jason Fisher

Aurora Energy LLC
Annapolis, MD
410-268-3088
jason at aurora-energy.com


-----Original Message-----
From: Mo Rousso [mailto:mrousso at heliopower.com]
Sent: Monday, September 29, 2003 2:41 PM
To: RE-wrenches at topica.com
Subject: Request re Inspector Training [RE-wrenches]

Greetings all,
>
I¹m doing a gratis Grid-tied PV workshop (1-1/2 hrs) for some City
Inspectors in San Diego County.  I¹m soliciting input regarding what you
consider to be important points to cover with them.  Basically, what
differentiates a good code-compliant installation from the fast bucks guys.
I have my standard spiel, but want to make sure I don¹t miss something
important.

TIA,
Mo
--
Mo Rousso
President
HelioPower
Renewable Energy Systems
Remote Power Solutions
mrousso at heliopower.com
www.heliopower.com
760.451.9374

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------





More information about the RE-Wrenches mailing list