ProSine 2.0 glitches [RE-wrenches]

Christopher Freitas - OutBack Power cfreitas at outbackpower.com
Thu Sep 25 13:46:57 EDT 2003


CVSOLAR at aol.com wrote:
> Any more comments good or bad on the ProSine 2000 watt with charger?

One real issue to watch out for on the ProSine 2.0 is that the transfer 
switch is only 30 amps and the charger is completely backed off at 24 
amps of pass thru AC loads (80% of the max input breaker rating I 
guess).Then the inverter not only does not charge but it actually starts 
consuming 5 amps DC from the battery.  The battery voltage drops even 
though the generator is running.     

Ezra/Roy - please verify this issue still occurs with the ProSine 2.0?

Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com  www.outbackpower.com
Tel 360 435 6030  Arlington WA USA

- - - -