Christopher,
Why the .9 derating factor?
I generally take a slightly different approach. I figure that a 48V 
inverter should pretty easily give full power down to about 44V. In 
that case it would be 3600/44*1.25=102.28. Either way, I agree that 
you should round up to the next available size of 175A. The only real 
downside is a jump from 1/0 to 2/0 cabling which I really don't have 
a problem with anyway.
Bob-O

>jay peltz wrote:
>>  Say with the 3648 do I use the same 100 amp breaker? or should I go with
>>  the next size up?
>
>The 100 amp breakers are somewhat acceptable but are at the limit:
>
>    3600 / 48 / .90 * 1.25 = 104 amps

-- 