Christopher Freitas - OutBack Power wrote:

> In order to say if a specific inverter system can run several motors we 
> will need an idea of the start-up current required by each of the 
> motors. If the actual start-up current is not available than the motor 
> size, construction and application can be used to get a fairly accurate 
> idea of what the start amps will be.  
> 
> Based on the ability of the two SW5548s being able to sometimes start 
> the large 7 hp motor,  I would say that a "QUAD" stack (four) of the 
> OutBack FX (sealed) or VFX (vented) series inverters (which version 
> depends upon installation issues and ambient temperatures expected). 
> The FX and VFX versions have the same motor starting ability, but 
> different continuous power ratings (2.5 sealed versus 3.6 kw vented).  
> The VFX has a larger power transformer in addition to the additional 
> airflow - hence the higher power.  
> 
> The X-240 autotransformer will help by keeping the two legs of AC 
> balanced and is also required when more than 2 inverters are connected 
> in the series/parallel configuration.  This trick with the X-240 
> autotransformer is only possible with the OutBack inverters - it will 
> not work with the SW series or other models. 
> 
> With the four OutBack inverters you will have 100 amps RMS / 140 amp 
> peak @ 240 VAC of starting current - this is about 25% more starting 
> current than a pair of SWs.  The X-240 autotransformer will also keep 
> the 120 VAC motors from overloading one pair of inverters when they kick 
> on - the start up current is split up onto all four inverters.  
> 
> The OutBack inverters also do not instantly trip off into overload like 
> the SW series (especially the SW5548s) but instead will supply the motor 
> with reduced AC voltage for up to 5 seconds.  This allows larger motors 
> to be started than one might expect from looking at the motor specs.  
> The AC voltage will however dip during this "soft start" process so the 
> lights will dim etc if they are connected to the same inverter as the 
> large motor.  
> 
> Another option is to look at a separate soft start control for the 
> larger motors.  i have had good luck with the Allen-Bradley STC 
> (starting torque controllers - although they changed the model names a 
> while ago).  The best ones I found were designed to start conveyor belts 
> or similar loads - they have an adjustable ramp time period and current 
> feedback which worked well with the SW series in a couple of my more 
> extreme installations.     
> 
> Christopher Freitas
> OutBack Power Systems, Inc.
> cfreitas at outbackpower.com  www.outbackpower.com
> Tel 360 435 6030  Arlington WA USA
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> 
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> 
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
> 
> 

-- 
Alaska Renewable Energy
981 Gold Mine Trail Fairbanks, Alaska 99712
Phone: 907-457-4299; Fax: 907-457-4290; Email: gegan at renewalaska.com
URL:  http://www.renewalaska.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------


</x-flowed>


More information about the RE-Wrenches mailing list