You should check the RMS voltage and peak AC voltage when the inverter 
is running with a light and heavy load.  The RMS voltage should be 
120VAC +/- 10V under all conditions but the peak voltage should be 
between 180V and 140V. There are a couple of failure modes that can 
result in the behavior you are seeing.  

Most likely it needs a new FET board. Getting someone with a O-scope to 
check it is probably the best way to check it.  

Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com  www.outbackpower.com
Tel 360 435 6030  Arlington WA USA
 
jay peltz wrote:
> 
> Hi All,
> 
> I've got a DR inverter that is doing the following.
> 
> When voltage above around 13.8v ( 12v system) the inverter will not run
> electronic items, it'll do lights and toaster etc, but not the TV, radio
> etc.
> 
> Any ideas?  or is this back to the factory?
> 
> thanks,
> 
> jay
> 
> Peltz Power
> 
> 
> 

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------



More information about the RE-Wrenches mailing list