Uni-Solar and SMA and Xantrex PV inverters [RE-wrenches]

Roy Dyngen roy.dyngen at xantrex.com
Tue Aug 19 12:04:57 EDT 2003


Joel,

As for nuisance breaker tripping or blown fuses, they would have to be 
sized to allow for the "soaking" period.  In particular to the PV series 
inverters, exceeding the 600 volt limit will cause a latching 
fault,(must be manually reset).  I spoke to Mike Behnke in Livermore and 
he said he had in the past suggested shorting out one panel per string 
during the soaking period to minimize the chance of overvoltage.  

Roy Dyngen
Joel Davidson wrote:
> 
> Uni-Solar modules have higher initial voltage and current. Has anyone
> experienced nuisance breaker trips or blown fuses during the first 8 to
> 10 weeks after installation?
> 



Roy Dyngen

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------



More information about the RE-Wrenches mailing list