Using transformers at other voltages and Frequencies [RE-wrenches]

Daryl Thayer daryl_solar at yahoo.com
Fri Aug 1 10:38:00 EDT 2003


Thanks to everyone 
For all the help with using a transformer at other
frequencies.  

It appears it will work, at increased losses, and at
one half the power at 30 cycles, by using 1/2 the
voltage.  My application is I was hoping to use the
upper end of the power curve of the wild AC from a
wind machine.  HOwever I will need larger
transformers. The Outback is rated at 4kW at 60
cycles, and then would be only 2kW at 30 Hz.
Thanks DAryl
--- Hugh Piggott <yahoo at scoraigwind.co.uk> wrote:
> At 4:32 PM +0000 29/7/03, aerofirewp wrote:
> >Daryl
> >
> >   I would disagree with Jim about 30 hz being a
> problem ,
> >because of the fact that you are also halving the
> input voltage.As
> >long as the volts/hz  is the same or less you will
> not saturate the
> >core and draw excessive magnitizing current.
> 
> I agree.  Halve the voltage and halve the frequency
> at the same time. 
> I do this quite often.  The transformer will work
> fine but it is true 
> that you can only put 1/4 the power through it at
> that voltage if you 
> want to keep the same % efficiency (the same % of
> the power lost in 
> the copper resistance).
> 
> Buy a bigger transformer if you need one.  No need
> for a special one, 
> so long as you watch the volts.
> -- 
> Hugh
> 
> http://www.scoraigwind.co.uk/
> 


__________________________________
Do you Yahoo!?
Yahoo! SiteBuilder - Free, easy-to-use web site design software
http://sitebuilder.yahoo.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------



More information about the RE-Wrenches mailing list