Allan:
 
NEC 690 also allows you to interconnect on the line side of the main
service disconnect.
This would avoid the need to find an obsolete breaker.
Just tap the lines feeding the load center and then install a fused
disconnect (allowed under tap rule) at the service location.
The disconnect then meets the requirement for the disconnect and has
overcurrent protection to boot.
Murray makes a NEMA 3R, 2 pole, 30 Amp, fused disconnect that is
service entrance rated - about $25.00.
 
 
 
 
If you have any questions or if I can be of any further assistance,
please to not hesitate to contact me.
 
Best Regards,
 
John Berdner


>>> allan at positiveenergysolar.com 7/14/2003 04:00:07 PM >>>
Wrenches,
I have done an initial site visit for a Sunny Boy system. The house has
two
Square D "Trilliant" load centers. There are plenty of breaker spaces
available, but no unused breakers. Our supplier says that the line was
discontinued by SqD about 5 years ago, and breakers aren't available
anymore. I'm not surprised--the stuff is all white plastic that looks
like
it was made for the cheapest kind of mobile homes.

Has anyone a line on a 2P 15A? Or a 2P 20A, or even a 1P 20A for an
1800? I
want to know if I can source a breaker before we offer a quote on a
grid-tie
system.

Thanks for any responses. Off-list replies are best:
allan at positiveenergysolar.com 

Allan Sindelar
Positive Energy






--
[Non-text portions of this message have been removed]

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================




More information about the RE-Wrenches mailing list