--- You wrote:
<I don't know why it is that Non-PV DC is allowed in the same raceway as
AC???? I can't run 120 and 480 in the same conduit....>
You can run 120 and 480 in the same conduit. See 2002 NEC 300.3(C) Conductors of
Different Systems, 200.6(D) Grounded Conductors of Different Systems, and
210.4(D) Identificationof Ungrounded Conductors.
<Why is it that PV is excluded anyway??? >
John Wiles explains in Photovoltaic Power Systems and The National Electrical
Code: Suggested Practices (December 1996) -"This requirement stems from the
need to keep "always live" PV source conductors separate from those that can be
turned off."
Hope this helps.
Dick Ratico