Different systems vs the same system (Was Conduit insidethe tracker pole)
Joel Davidson
joeldavidson at earthlink.net
Tue Jun 17 22:43:10 EDT 2003
It is a good idea to educate your local electrical inspector beforehand and
get his agreement. Rework to pass inspection is a drag and being "right"
makes the rework an even more unpleasant experience. The inspector is always
right - if you want a fast sign-off.
John Berdner wrote:
> Ahhhh Matt:
>
> This comes up fairly often so we cover this in our installer training
> seminars.
> I too misinterpreted this section of the Code but J. Wiles straigtened
> me out on this one.
> The Code is saying don't run the waires to your washing machine in the
> same raceway as you PV output circuit.
> This makes sense to me.
>
> In a PV system the ac and dc we want to run together are part of one
> system - The PV system.
> The 690.4(B) says "different systems" which we dont got none.
> Also, the conductors mentioned in 4B are connected together in the
> inverter.
> The PV system (singular) can include one or more inverters, and one or
> more sub-arrays.
> If the inverter also included batteries then they too are part of the
> same PV system.
> I believe this means you could also run the battery cables in the same
> raceway as the PV and AC in and out.
> Of course you would have to use battery cables rated for use in conduit
> and with insulation rated for the highest voltage.
>
> Best Regards,
>
> JSB
>
> >>> mlafferty at universalenergies.com 6/16/2003 05:05:23 PM >>>
>
> Allan Wrote:
>
> >Per NEC 300-2 (c) (1), AC and DC circuits are permitted inside the
> same
> enclosure, cable, or raceway.
> >Or am I missing some fine print elsewhere?
>
> All:
>
> Brother John B's response gave me a very big sigh of relief... Since I
> know he knows... Maybe they finally got that nasty little exception
> out
> of 2002 and I missed it.... Had to look.
>
> The "fine print" is in the Exception.... Exception: For solar
> photovoltaic systems in accordance with 690.4(B).
>
> 690.4 Installation.
> (B) Conductors of Different Systems. Photovoltaic source circuits and
> photovoltaic output circuits shall not be contained in the same
> raceway,
> cable tray, cable, outlet box, junction box, or similar fitting as
> feeders or branch circuits of other systems, unless the conductors of
> the different systems are separated by a partition or are connected
> together.
>
> Therein lies the basis for my reference in the previous post.
>
> I've had some real challenges in the not too distant past with this
> one... You try getting 5 "systems" (2 PV DC, 3 AC)
> into, through, and back out of a 4" x 6" x 4' gutter when the UNION
> ELECTRICIAN who was supposed to be doing the project just kind of
> didn't
> want to finish.... Likely due to the fact he REALLY screwed up on his
> in-wall conduits and their arrangement.
>
> Well, guess who gets to push brooms.... Hey, it actually really looks
> terrific inside and outside the gutter and works well, to boot. On
> top
> of that, tough inspector... LOVED it! Points! Bingo!
>
> Maybe the "ol' fat guy with the big mouth" hasn't lost it, after all.
> lol
>
> Pray for Two Palm Trees and a Hammock!
>
> Matt Lafferty
> Universal Energies Institute
> mlafferty at universalenergies.com
> (916) 422-9772
> (916) 628-7694 Cell
> (916) 914-2247 Fax
> www.universalenergies.com
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
> --
> [Non-text portions of this message have been removed]
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-Wrenches
mailing list