Ken / Wrenches:

Regarding the "Code Issues" associated with running "unprotected
conductors" inside the tracker pole:

1. As long as the entrance to the pole is properly bushed and the pole
is grounded, this application is generally suitable. (Signs have been
installed without internal conduit in the poles for many years.  The
pole serves as the raceway.)

2. Although admirable, internal conduit is not required unless there are
multiple sources of electricity in the same raceway.  (I.E. AC & DC)

3. Vertical support of the conductors internally is generally not "an
issue" due to the relative short height of most trackers.  If you are
going up 100', then you get into a situation...  NEC 300.19 and the
associated table address this.  

2-Cents for Sunshine!

Matt Lafferty
Universal Energies Institute
mlafferty at universalenergies.com
(916) 422-9772
(916) 628-7694 Cell
(916) 914-2247 Fax
www.universalenergies.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================






More information about the RE-Wrenches mailing list