Jeff asks:
Any reason an HU361 couldn't be used as a 2 string (or even 3 string)
combiner/disconnect for a single SB? (as long as the combined
string amperage is below the "fuse rating" of each panel?)
Wired as follows:
________ + to SB
l l
0 0 0
0 0 0
l l
l l
l l
+ + from String 2
from String 1
Jeff / Wrenches:
The HU361 is my "disco of choice" for a number of reasons. There are
two potential issues I see with your proposed schematic...
1. The Line (Array) is required to be landed on the top lugs of the
Disco. (Behind the arc-shield)
2. The lugs are rated for single-conductor landing only.
My recommendation, at least relating to the Disco at the Inverter, is to
run the two "switched hots" (from the bottom lugs) to the SB. The SB
has 3 DC Input terminals for a reason. This is it.
Regarding the use of an HU361 at dual locations, I think you will find
you can easily run the extra pair between disconnects in the same
conduit you are already installing.
Try it this way:
ARRAY
+ from String 1
+ from String 2
l l
0 0 0
ROOF Disco
0 0 0
l l
l l
l l
+ + to 2nd Disco; Line 3
to 2nd Disco; Line 1
l l
l l ________ IN CONDUIT
l l
+ from Roof Disco; Load 1
+ from Roof Disco; Load 3
l l
0 0 0
INVERTER DISCO
0 0 0
l l
l l
l l
+ + to SB DC Input
to SB DC Input
Hope this helps...
Pray for Sun and No Tanlines!
Matt Lafferty
Universal Energies Institute
mlafferty at universalenergies.com
(916) 422-9772
(916) 628-7694 Cell
(916) 914-2247 Fax
www.universalenergies.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-Wrenches
mailing list