Thanks for the feedback. The PSI article on Ufer Grounding was
particularly interesting. It seems that the Ufer concrete ground "can" be
an effective method, but only if done right.
From the NEC
250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2
in.) of concrete, located within and near the bottom of a concrete
foundation or footing that is in direct contact with the earth, consisting
of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other
electrically conductive coated steel reinforcing bars or rods of not less
than 13 mm (½ in.) in diameter, or consisting of at least 6.0 m (20 ft) of
bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be
permitted to be bonded together by the usual steel tie wires or other
effective means.
So, a typical pier and pad foundation with a 5- 6 foot square pad would not
meet NEC's requirement to have a 20 ft minimum length of rebar. It's
not clear from the code whether or not the 20 feet of Cu ground wire would
be in compliance if it were snaked or threaded back and forth in a 5-6 ft
square concrete pad.
Another concern is the structural integrity of the foundation. Rohn says
all rebar has to be covered by at least 3 inches of concrete but the Ufer
method would have one piece of rebar extending up and out from the
foundation to provide an attachement point for the ground wire that then
attaches to the tower leg. Would the exposed rebar create a path for
moisture that would lead to cracking from the freeze/thaw
cycle? Probably no more so than the embedded
reporters...errrr...J-bolts for the tower. Perhaps if we added an extra
piece of rebar specifically for this purpose, then it would be ok.
If we build a foundation that allows a 20 foot rebar rod, I may be tempted
to try the Ufer method. (see HP#75 Page 11 for one such example) but I
would probably sink conventional ground rods too. For a regular pier and
pad foundation, it seems like ground rods are the way to go.
Dave
----------------------------------------------------------
David Blecker, P.E., Director
Seventh Generation Energy Systems
608-424-1870 (ph) 424-1810 (fax)
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
</x-flowed>
More information about the RE-Wrenches
mailing list