Jay,
My experience is that manufacturers have universally not paid much attention
to this issue as seen with the various lame grounding methods that they
allow according to their listing.
The listing only allows connection at the grounding point. That's a real
pain for roof mounted systems. I've gotten fed up with manufacturers being
unresponsive and have started teach people to use lay-in lugs on the end of
the module for ease of installation. Manufacturers have all kinds of
heartburn when you start drilling holes in the end of their modules, but
maybe that will drive them to drilling the hole for us.
Bill.
-----Original Message-----
From: Jay Peltz, Peltz Power [mailto:jay at asis.com]
Sent: Monday, April 21, 2003 11:09 AM
To: RE-wrenches at topica.com
Subject: Re: Where is Ground Clamps [RE-wrenches]
Hi John and Bill,
OK, so here is my question.
I'm holding in my hand a "grounding screw" from Sharp/Schott. This screw is
SS, is machine thread, and is really really small. It is so small that it
will rattle around in the listed grounding hole. Yes it has a star washer.
How is using this any different than installing a star washer on the frame
either under the mounting frame or a surface attachment for the top down
style?
And if the manufacture gives me a grounding screw, can I use anything else
without voiding the UL warranty? If so, can I install the ground anywhere,
or do I have to use the approved grounding hole?
Thanks
jay.
----- Original Message -----
From: "John Berdner" <jberdner at sma-america.com>
To: <RE-wrenches at topica.com>
Sent: Monday, April 21, 2003 10:55 AM
Subject: RE: Where is Ground Clamps [RE-wrenches]
> Jay:
>
> The problem with grounding through the frame is that many of the frames
> are anodized aluminum (read as excellent insulator). Unless the
> structure has been evaluated as a grounding member you can't rely on it
> to provide the equipment ground. I think this could be solved with
> insulation piercing hardware, e.g. star washers, but so far none of the
> structure manufacturers has developed this concept to the point that it
> can be listed as a means of grounding. In absence of Listed "systems"
> that provide equivalent grounding means, the Code says you have to run a
> ground wire to every module to make sure it stays grounded. The UL
> requirement for a ground is 0.1 Ohms at 60 Hz. Given that we are
> talking about dc I think UL would also want to see a dc impedance
> measurement as well.
>
> Based on my own experience I have measured grounding impedances far
> above this level when using only the frames for grounding. Others such
> as J. Wiles and B. Brooks have also confirmed high ground impedance on
> frames when only the structures are used. Until we have a grounding
> structure system I think you have to run a ground wire (even one long
> one daisy chanied) to every module. Also, J. Wiles has convinced me
> that all splices in the equipment ground wires should made with "non
> removable" pressure connections, i.e. butt splices or ferrules. Just my
> $0.02.
>
> If you have any questions or if I may be of any further assistance,
> please do not hesitate to contact me.
>
> Best Regards,
>
> John Berdner
>
> SMA America, Inc.
> 12438-C Loma Rica Road
> Grass Valley, CA 95945
> 530.273.4595 - Tel
> 530.274.7271 - Fax
>
> -----Original Message-----
> From: Jay Peltz, Peltz Power [mailto:jay at asis.com]
> Sent: Monday, April 21, 2003 09:50 AM
> To: RE-wrenches at topica.com
> Subject: Re: Where is Ground Clamps [RE-wrenches]
>
> Hi Dean,
>
> Can you give me the code # that states all panels must be grounded in
> addition to the metal frame they are on?
>
> One installer I know puts in the permit all grounding to be done in
> accordance with 250.136(a). This allows for only a single ground wire
> from
> each seperate array. Makes it much easier.
>
> thanks,
>
> jay
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-Wrenches
mailing list