Lightning arrestors [RE-wrenches]
Robert Warren
robertwarren at mail.com
Tue Mar 11 02:30:27 EST 2003
I just recently had to replace the AC control boards on two paralleled
Trace SW4548E inverters because Xantrex would not warranty them, even
though they were only halfway into their two year warranty period. This
repair cost me nearly as much as the price of one new inverter!
They said, "because the same fault was found on both inverters, it was
likely an external cause." Now, both inverters were still working as far
as inverting: it was the battery charger mode which was bad. First clue
was that the internal LCD meter showed 0 VAC output when the inverter
was really putting out 228 VAC. So if the inverter didn't know if it was
producing any power, how could it synchronize to the generator when it
started?
I think it is really bad news for dealers that there is no internal
surge protection inside these inverters. Sunnyboy inverters have a bank
of MOV's and multi-path surge protection, as far as I know.
The technie I talked to on the help line said that the particular
chip, T5, could have been damaged by a spike or a high demand. This
could have been lighting, or could have been a spike from the gen set.
Since the Trace inverters have both software and hardware overcurrent
protection, this led me to believe it was a spike. Further analysis
before sparking them up again revealed a corroded through grounding
clamp bolt. Everything was properly earthed to a single point grounding
system when installed, but I think there was still a bit of ground-loop
current between the house and the barn, where the generator sits,
accelerated the di-electric effect on this brass bolt. Once the closest
Earth to the generator was lost (even though it had another oversized
grounding wire back to the main earthing rod for the inverters) the
genny was likely throwing out spikes.
I just hate lifting those heavy Trace monsters up on the wall, and
don't want to do all this again! So I installed a couple of lightning
surge suppressors parallel to the AC2 input to protect the inverters
from the diesal generators, and another on the AC out circuit, just in
case I get an induced lightning spike coming back from the house.
Robert Warren
robert.warren at solarcentury.co.uk
www.solarcentury.c.uk
What will we do if there is another fuel shortage?
Did you know that there is a pollution free, completely
renewable fuel which you can use right now in your own car?
Don't replace the engine, replace the fuel.
Check out my website on making your own fuel:
http://running_on_alcohol.tripod.com
robertwarren at mail.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-Wrenches
mailing list