C40's and SW's [RE-wrenches]
Bill Brooks
billb at endecon.com
Wed Feb 5 19:27:47 EST 2003
Eric,
I believe several of the posts mentioned that sell voltage must be lower
than the charge controller float and bulk voltages to work properly.
Something that has not been mentioned that you point out here is that if you
are using the Grid Usage Timer to sell power, the sell voltage is not
temperature compensated--it is a constant.
However, if you are in sell mode with the Grid Usage Timer turned off (start
and stop times identical), then the SW will go to float charge setting and
remain there--this is a temperature compensated setting.
So to sum up:
1. Turn Grid Usage Timer Off (that is default)
2. Turn Bulk Charge Timer to 0:00 (default is 2:00)
3. Leave Float voltage setting at the default of 53.6 Volts
4. Set your backup charge controller to at least 1 Volt higher (54.6V)
(and confirm that the setting is accurate)
5. Make sure all equipment has temperature compensation probes and the are
attached to the battery such that they are reading as close to the same
temperature as possible.
Bill.
-----Original Message-----
From: Eric Smiley [mailto:Eric_Smiley at bcit.ca]
Sent: Wednesday, February 05, 2003 3:29 PM
To: RE-wrenches at topica.com
Subject: RE: C40's and SW's [RE-wrenches]
I didn't see any mention of the SW Sell Voltage in the posts, which has
to be less than the C40 bulk and float voltages, but greater than the SW
float voltage.
However, (I believe it was Bill that pointed this out to me) the Sell
Voltage is not temperature compensated.
Eric Smiley
Project Leader
Photovoltaic Energy Applied Research, Technology Centre
British Columbia Institute of Technology
Burnaby Campus
NE25 - 3700 Willingdon Avenue
Burnaby, British Columbia
Canada V5G 3H2
phone: 604.432.8657 fax: 604.436.0286
esmiley at bcit.ca www.tc.bcit.ca
The information contained in this E-mail is intended for the addressee
only. If you have received this in error please delete it.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-Wrenches
mailing list