1 - Check for correct wire size.
2-Try looking at all of your wire path connections including the ones in the
generator, junction boxes. I have seen this in both AC and DC circuits. The
voltage flows but there is no current due to a corroded or burnt connection
and the inverter goes into bulk and then drops out due top HZ going out of
spec. or voltage fluctuation. You may want to swap out circuit breakers one
at a time too, as one "may" be torched internally.
Best of luck
Dana
Responsible Technologies for Responsible People.
Great Solar Works, Inc.
slrwrk at ocinet.net - 970.626.5253
Ridgway, CO, USA
- - - -