Lee,

You cannot assume the same temperature difference occurs all the time at low
temperatures. To be sure, the steady-state temperature differences should be
nearly identical. The problem is a very cold morning with cloud cover that
instantly goes away as when a high pressure system moves in. This is when we
measure the highest open circuit voltages. It usually only happens
occasionally, but damage due to overvoltage may only take a few seconds.
Better to be sure that the voltages are such that 600 Volts can never happen
under any circumstance.

Bill.

-----Original Message-----
From: solplex at montana.com [mailto:solplex at montana.com]
Sent: Friday, November 01, 2002 12:02 PM
To: RE-wrenches at topica.com
Subject: SPAM: PV Inverters module strings [RE-wrenches]


Bill Brooks.  Bill, I remember your presentation at a Schott grid-tie
class and you seemed to have a good handle on some of this stuff.  To
figure out panel voltages we need to figure out the temperature at the
panel.  All sorts of numbers are used to describe the difference between
ambient and panel temp, and in general the difference between summer hot
ambient and panel temp is assumed to be the same as the difference
between cold ambient and panel temp.  Is that a reasonable assumption?
And what are reasonable estimates for these ambient/panel differences?

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================







More information about the RE-Wrenches mailing list