Module grounding revisited [RE-wrenches]

Nick Nicholas APS at SBCGLOBAL.NET
Wed Oct 30 01:25:55 EST 2002


Brad:
    The NEC does not allow #8 solid wire to be used as a grounding electrode
conduct unless it is protected by conduit.  #6 is allowed on the outside of
a structure  or building if it is free from physical damage.  If the
grounding conductor is exposed to severe physical damage, #4 is required.
NEC 250.64

Alternative Power Systems
www.alternativepowersystems.com
aps at sbcglobal.net
135 Colfax Ave.
Grass Valley, CA 95945
(530) 274-0588 phone
(530) 274-0589 fax
----- Original Message -----
From: "Brad Bassett" <bsbassett at earthlink.net>
To: <RE-wrenches at topica.com>
Sent: Tuesday, October 29, 2002 7:43 PM
Subject: RE: Module grounding revisited [RE-wrenches]


> The trick is get electrical contact between the module frame and the
> rack. Many modules frames are so well anodized that electrical contact
> can't be counted on by just bolting them together. There must be a way
> to break through the anodized coating to get contact.
>
> One method used by some is to put a star washer (stainless of course)
> between the module frame and rack where it is bolted down. Whether this
> gives adequate conductance or not I'm not sure. I also wonder how it
> will do over a period of years. It also wouldn't work with a clamp down
> type rack.
>
> Another corollary issue is how to get a good, long lasting ground on any
> aluminum rack or module. Somewhere there is likely to be a problem with
> corrosion between the aluminum frame and the copper grounding wire.
> Inserting something stainless between might slow it down some. The best
> I've seen is a copper lug (GBL-4DB from Ilsco) held with a stainless
> bolt with a stainless washer between it and the aluminum frame (with
> copper ground wire of course).
>
> I have a question about the size of the ground wire. I think I've read
> in the NEC that AWG #6 stranded or #8 solid is required where subject to
> physical damage. Does ground wiring in an array qualify as subject to
> physical damage (if the combiner is adjacent)? Or is #10 ground wire
> adequate? Since #10 or smaller interconnect wire seems to be accepted,
> maybe that's all that's needed for ground wire. Any thoughts?
>
> Thanks
> Brad Bassett
>
> William Miller wrote:
> One concept I had been wanting to research is that of grounding
> > only the rack frame.  The Code seems to allow this:
> >
> > (A) Equipment Secured to Grounded Metal Supports. Electrical equipment
> > secured to and in electrical contact with a metal rack or structure
> > provided
> > for its support and grounded by one of the means indicated in 250.134.
> >
>
>
> Brad Bassett
> bsbassett at earthlink.net
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-Wrenches mailing list