SW error messages [RE-wrenches]
Bob-O Schultze, Electron Connection
econnect at snowcrest.net
Wed Aug 28 11:01:21 EDT 2002
<x-flowed>
William, etal,
One of my dealers reported this same problem to me. IT ONLY showed up
if you were using the SW to start/stop a genny. It was a Input Relay
error when the SW shut the genny down after a charge cycle. The thing
that made it unacceptable was that it also turned the inverter off
and required a manual restart. No good.
Apparently it was in firmware, not hardware and the new rev has
solved that particular problem. There may be others I'm not aware of.
Bob-O
>Friends:
>
>I have a customer who has seen two error messages that I am not quite sure
>what they mean:
>
>1. Input relay error.
>
>2. Generator sync error.
>
>Message number 1 is not listed in the manual. Message number 2 is listed
>and indicates that voltage or frequency were out of tolerance. This is
>unusual as this system is connected to a new, robust Onan 20KVA water
>cooled unit that has never shown any of these problems.
>
>I'd call Xantrex, but the last few times I've called I've received
>information that was vague and contradictory. I know this is the luck of
>who I reach and what their expertise is, but it does not encourage one to
>wait on hold if the results may not be worth the wait.
>
>Thanks in advance.
>
>William Miller
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-Wrenches
mailing list