See if the local battery place will loan you 24 volts worth of good
batteries.  They don't even have to be 6 volt ones.  For testing purposes
even starting batteries will work. You might have those laying around.  Then
test the system while watching the battery voltage and the controller output
voltage.  That will tell you a lot.

or even better, walk away.

Travis
----------
>From: "Bob Ellison, Alternative Energy Systems" <ellison at gisco.net>
>To: RE-wrenches at topica.com
>Subject: RE: Can this happen???? [RE-wrenches]
>Date: Mon, Aug 26, 2002, 3:19 PM
>

>At the very least if you want to put a meter on the battery bank, I bet you
>will see the voltage drop through the floor under the pump load.
>1 hour @ 20 amp charge puts 20 amps into a set of dead and probably sulfated
>batteries that I assume are rated for at least 200 Ah.
>(You might want to check my math, these complex calculations sometimes throw
>me).
>
>How long does he think the pump will run on a 20 amp charge? At the least
>give them a 10 - 15 hour charge on a standard taper type charger then see
>what happens.
>
>My bet? Nothing until he replaces the batteries.
>Then you can find out what else he has done incorrect / cheaply, or just
>plain wrong!
>I assume solar charging, has he got a working controller? What boiled the
>batteries dry, or did the electrolyte evaporate in the heat???
>
>"Was told by industrial electrician that it is *possible* for battery
>banks like this one to have sudden voltage drop and current spike that
>would blow a 10k resistor. Can this happen?"
>
>I have to bet on the voltage drop, that's almost a guaranteed event.  Don't
>know about the 10K resister but it might be possible... Is there one in the
>pump?
>
>Later,
>Bob
>
>
>RE. Ellison
>Supplier of;
>Alternative Energy Systems & Supplies
>34642 Countryman Road
>Theresa, NY. USA
>                               13691-2076
>
>
>-----Original Message-----
>From: Holt Kelly [mailto:hkelly6 at msn.com]
>Sent: Monday, August 26, 2002 3:34 PM
>To: RE-wrenches at topica.com
>Subject: Can this happen???? [RE-wrenches]
>
>
>Scenario:
> -Sunrise pump, 4-6v battery bank -golf cart (24v), home owner installed
>all but pump(wince).
> -While prepping pump to drop, noticed home owner making several trips
>to pump house with 1 gal. jugs of water. ("yup, they are bone dry"). My
>guess is for atleast 6 mos. but not sure.
> -Found 1 battery to have hole in it. ("Uncle Gus has some new ones,
>I'll be back in an hour".) Instructs me to go ahead and drop the pump
><should have walked away- but that's another story>.
> -Home owner "slam dunks" battery charging. About 1 hr. on 20a a/c
>charger.
> -I recommend to check with battery mfg. about charge rate and mixing
>new w/ old.("They're OK. Read 25.4v across the lugs")
> -Pump at 175', static is 132'
> -Pump runs for about 20 seconds and stops.
> -Meter reads no continuity between pump conductors.
> -Was told by industrial electrician that it is *possible* for battery
>banks like this one to have sudden voltage drop and current spike that
>would blow a 10k resistor. Can this happen? Any other ideas?
>
>
>
>Holt E. Kelly
>Holtek Fireplace & Solar Products
>Waco, TX.
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
>
>
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-Wrenches mailing list