I do not understand that statement (below). In a series circuit you interrupt the
circuit at any point and current no longer flows. On a floating system the current
is "live" only with respect to the other conductor. So why would you need over
current on both wires?
Todd
Hugh Piggott wrote:
> The overcurrent devices are there in case of a fault. You only need
> one overcurrent device when you ground one conductor. You only have
> one live conductor left to worry about. If the system is floating
> then both conductors are potentially live, and need protection.
- - - -