DC-GFP/2 protection [RE-wrenches]

Electrical Energy solar at eagle-access.net
Thu Aug 22 13:15:27 EDT 2002


<x-flowed>
You Wrote:

"How is the "system" becoming ungrounded when
you disconnect the array? "

I also can't see how the grounding would be affected by using the GFP/2 as 
an array disconnect.   Looking at the Outback schematic, the array negative 
goes to the negative bus, which connects to the batteries.  If the negative 
bus is properly grounded, the array negative will remain grounded as well.

I also don't see the need for the ground fault protection, especially the 
way it is set up.  It seems to fulfill a code requirement, without giving a 
substantial increase in safety.

May be I'm missing something?


Drake


  At 12:02 PM 8/22/2002 -0500, you wrote:
>----------
> >From: jberdner at sma-america.com
>
> >Yes, if you use the GFDI breaker as a disconnect then the system becomes
> >ungrounded when you disconnect the PV.  Here in the US, many of the code
> >
> >
> >Best Regards,
> >
> >John Berdner
>
>
>Ok, I'll admit that I'm not following this to well, plus I have done so few
>roof mounts I'm not up on Ground Fault protection for solar arrays.  Given
>that I have my first installation with these  DC-GFP/2's is coming up soon I
>need to ask some questions.  How is the "system" becoming ungrounded when
>you disconnect the array?  Perhaps I don't understand what you mean by
>"system".
>
>Looking at the PSDC diagram on page 29 of the "Outback Catalog and System
>Design Handbook".  Thanks to Outback for sending that by the way.  Pretty
>handy book for those who don't have one yet.  I see the wiring method and
>the negative array is not involved. Right?  There appears to be a breaker
>per sub-arrray with each one feeding the the bottom of the DC-GFP/2 breaker.
>  The two poles on the output side of the DC-GFP/2 then feed two charge
>controllers which then are connected to the positive buss via two more
>breakers.  The good news is that at least the DC-GFP/2 is a two pole unit.
>
>Whew, seems like a lot of hassle for Ground Fault protection which I (and
>many others) never have quite grasped the need for.  How does a breaker in
>the load center stop the array from feeding the fault which is somewhere
>between the array and load center?  I can see how GFP stops the battery from
>feeding the fault when it's only a low amperage, intermittent fault which
>probably wouldn't trip the Charge controller's breaker.  I'm sure if it was
>explained to me I would understand it better.
>
>
>Thanks
>Travis Creswell
>Ozark Energy Services
>----------
> >From: Christopher Freitas  -  OutBack Power <cfreitas at outbackpower.com>
> >To: RE-wrenches at topica.com
> >Subject: RE: DC-GFP/2 protection [RE-wrenches]
> >Date: Thu, Aug 22, 2002, 10:28 AM
> >
>
> >The OutBack DC-GFP/2 actually includes two 70 amp breaker poles in its
> >current form.  This was required by the breaker manufacturer to allow
> >them to mark the assembly as a "UL Listed" device.  The amperage is 70
> >to allow for coordinated tripping if an overload occurs (the DC-GFP will
> >not trip first - the 60 amp breaker will trip instead).  We are
> >considering eliminating the redundant overcurrent protection in the
> >DC-GFP but it does offer some benefit if it is not installed properly.
> >
> >John Berdner is correct that much of the world does not ground the
> >negative conductor and that grounding probably causes as many problems
> >as it solves.  In the US you can operate low voltage (less than 50 volts
> >DC) ungrounded - BUT - then you need breakers in both the negative and
> >positive conductors as they are both now ungrounded.
> >
> >Given the low cost of breakers and the space in our PSDC enclosure to
> >mount up to 16 breakers - I think that the extra breakers are a
> >reasonable addition to ensure safe installations.
> >
> >Christopher Freitas
> >OutBack Power Systems, Inc.
> >cfreitas at outbackpower.com  www.outbackpower.com
> >Tel 360 435 6030  Arlington WA USA
> >
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================



</x-flowed>


More information about the RE-Wrenches mailing list